www.thepetrosolutions.com

BMS Heaters Firing Control

Home Forums Petro Solutions Forum Energy Management BMS Heaters Firing Control

Viewing 2 reply threads
  • Author
    Posts
    • #1417
      Abu noor
      Moderator

      In BMS heaters which is better, more accurate,not hunting and good for turning?
      1.connected temperature controller with Fuel gas controller
      1 . Connected temperature with low selector.

    • #1425
      Nasir Hussain
      Keymaster

      Dear Zayed, Generally, the temperature controller is cascaded with fuel gas pressure to control the reactor inlet temperature. This setting is better with fine control of both temperature and fuel gas pressure.

      For further discussion, please upload the file with a size less than 1MB=1000KB by compressing the file or selecting the file of a smaller size.

    • #1427
      Abu noor
      Moderator

      As we discussed earlier here attached sketch for heaters firing control.

      Attachments:
      You must be logged in to view attached files.
Viewing 2 reply threads
  • You must be logged in to reply to this topic.